    Post

    Can anyone tell me if i made a mistake somewhere?
    600V 3 phase delta dropped down to 240/120V
    that will be feeding a small shop.
    Load
    1 50A welder @ 240V = 12000VA
    1 30A trailer @ 240V= 7200VA
    8 15A circuits@ 120V= 14400VA
    1 15A lighting@ 120V= 1800VA
    1 100A future @ 240V= 24000VA
    --------
    59.4KVA full load
    I could use 55KVA X-MER
    55KVA/(600*1.732)=52.92*125%=66.15
    Table 2 = #4awg primary cable
    overcurrent protection=52.92*125%=66.15A
    therfore A 70A c/b would be used.
    SECONDARY
    55KVA/240V=229A*125%=286.45
    Table 2 = #300awg secondary cable
    1/0 equipment ground.
    300awg will be brought out of the building and into a 225A splitter then out of the splitter into a fused disconnect and then into a 225A panel (bus rating)
    what size of cable and fuses should i use once i leave the splitter and am I missing anything?
    Thanks mosman

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Hi Mosman,

    It appears that you have calculated the primary correctly, however, the secondary has been calculated as if it were a single phase circuit.
    <BLOCKQUOTE><font size=2 face="Verdana, Helvetica, sans-serif">quote:</font><table border="0" width="90%" bgcolor="#333333" cellspacing="1" cellpadding="0"><tr><td width="100%"><table border="0" width="100%" cellspacing="0" cellpadding="2" bgcolor="#FF9900"><tr><td width="100%" bgcolor=""><font size=2 face="Verdana, Helvetica, sans-serif">"dropped down to 240/120V"</font></td></tr></table></td></tr></table></BLOCKQUOTE>
    Did you intend to run a 120/240 volt single phase feeder to the splitter?

    Ed

  3. #3
    Inactive Member mosman's Avatar
    Join Date
    November 24th, 2002
    Posts
    14
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Hi ed thanks for responding
    yes I do intend to run a single phase feeder to the splitter because of the welder is a 50A 240v unit and I don't think that it would work properly on 208V (right?!?!?!)the trailer also has a 30A 240V panel.
    Thanks
    Mosman

  4. #4
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Dropping down to 240/120 as opposed to 208/120 may cause you some capacity and balancing problems with your xformer.
    Check out this link for more info.

    http://www.federalpacific.com/univer.../chapter3.html